if you test the RCD again , you'll probably get lower readings. if it's not tripped for a while it could have got a bit sticky.
 
the earth loop can be massive with an rcd in line, well over a 1000 ohms and still comply

One would never accept a high earth loop reading on a TN system though, simply because it has an RCD in-line. If it's high, then there is either a fault, or the system wasn't designed very well.
 
the earth loop can be massive with an rcd in line, well over a 1000 ohms and still comply

Not for me I'm afraid. I always design to meet the MCB disconnection times on TN systems. I certainly don't put all my faith in the RCD to be happy with resistances that high.

E54 will have something to say about that too, I'm sure!
 
Not for me I'm afraid. I always design to meet the MCB disconnection times on TN systems. I certainly don't put all my faith in the RCD to be happy with resistances that high.

E54 will have something to say about that too, I'm sure!

What can you say to statements like that?? He's just another brainwashed fella that considers RCDs as the electricians cure all for badly designed and/or installed electrical work that don't/can't meet primary Zs values!!
 
the earth loop can be massive with an rcd in line, well over a 1000 ohms and still comply with meeting required disconnection times

If you'd included the bit in red you'd be correct in theory.....in practice though an earth loop that high (and the reasons for it being that high) is not going to comply with anything else.
 

Reply to Need confirmation on Zs results. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
890
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top