If you really wanted to to it backwards, this is how you would go about it:
Start with your cable characteristics, and if you look up the 18th wiring regs Table 54.2/3/4/5 you can pick as 'k' value for your start temp and cable types.
Let us assume you are running fully loaded at 70C and have 90C thermopastic insulation so the
short term max conductor temperature is 160C before damage. Then for copper you have k = 100
Reversing the usual equation we have:
sqrt(I2t) = S * k = 5.261 * 100
So I2t = 526.1 ** 2 = 27.7k (units of A2s)
Now we need to find what current for our OCPD will result in this let-through energy. For the usual graph of log(time) against log(PFC) there are straight lines of constant I2s we can plot. So we can find two points and then use a ruler to draw it. So
1 second => I = sqrt(I2t / t) = 526.1 / sqrt(t) = 526.1 Amps
10 seconds => I = 526.1 / sqrt(10) = 166.4 A
100 seconds => I = 526.1 / sqrt(100) = 52.6 A
Alternatively
10A => t = 27.7E3 / 10**2 = 277 seconds
100A => t = 27.7E3 / 100**2 = 2.77 seconds
1000A => t = 27.7E3 / 1000**2 = 0.0277 seconds
10kA => t = 27.7E3 / 10000**2 = 0.000277 seconds
So what OCPD do we have? Let us assume a 63A BS88 fuse of the 22x58mm size:
From this graph we can see that the 63A fuse curve intercepts our constant I2t line at around 1kA fault current. So if our PFC is above 1kA then the cable is safe as the fuse disconnects fast enough, if below 1kA then the cable overheats.
If you know your supply voltage range then from the minimum voltage you can compute your maximum Zs at the cable end for 1kA PFC, and then from your supply Ze you know your maximum R1+R2 to have the prvious Zs value, and from R1+R2 and the cable resistance per unit length, you can compute the maximum length.
[automerge]1598816704[/automerge]
If you are using a MCB or MCCB you really need to look up the manufacturers data as they all vary a bit. For example if you had a Hager industrial MCB of the B-curve type they provide this graph of let-through energy:
Going back to the previous numbers, we see that 27.7k A2s actually has two solutions, at around 250A (when it just enters the magnetic trip region) and again at around 4-5kA fault current. So here you need to have a low enough Zs to hit 250A (probably OK) but not so low that you hit 4-5kA or more.
So there might be a
short cable range where it would fail!