So you can use the tabulated values from, for example, UK regs provided the type of conductor and insulation are comparable. Most likely they are as Cu & PVC or XLPE is pretty much common use world-wide.
In this case above 10kA and the breaker might explode. That is the MCB's max interrupt capacity.Above 10ka the wire overheats even if the breaker opens on its magnetic trip? In essence BS7671 addresses this?
The max running temp here is also usually 70C or 90C, but that is for prolonged use. You hope that a fault is only a couple of seconds long at most, hence the higher value is tolerated for this method.My starting point is either 60*C or 75*C. In the US PVC is rated for 90*C.