Need help with wiring connections | on ElectriciansForums
Discuss Need help with wiring connections in the Central Heating Systems area at ElectriciansForums.net
Hi I am having trouble getting a boiler to fire up on the central heating.
I'm using a danfoss rmt 230 room stat ( connections 1, 2, 3, and 4
A Danfoss Ts715 Si programer L and N supply to electronics 1 Com , 2 N/C, 3 spare and 4 N/O
a worchester Greenstar 24, Boiler L and N supply to Boiler, Ls, Lr, Ns,
I have wired the stat to numbers 1 and 3
The boiler has its own live and neutral which is feed via as 3 amp fused spur, this also feeds the progamer L and N.
I have take the ls from the boiler to the common on the programer and then connected the
N/O (Terminal 4 on the programer) to terminal 1 on the room stat then connected terminal 3 on the room stat back to lr on the boiler.
Is this correct and do I need a neutral connected at the stat.
roomstat works better with neutral connected,if terminal 4 on programmer is on,and you have no voltage present at roomstat,then faulty programmer/wiring to it,if present and roomstat calling for heat then 230v at lr in boiler it should work,stat on boiler turned to heating and hw?
Hi, it's terminal 2 on the room stat that goes to the Lr in the boiler. 1-common, 2-on, 3-off and 4 is for the neutral I think.
Hi. yea your right bob22. but you don't need a neutral unless its an electronic stat. anyway i'd stay away from anything danfoss in my experience i've always found them crap
Reply to Need help with wiring connections in the Central Heating Systems area at ElectriciansForums.net
Certainly is!! And another thing .......... On the old Hive receiver the relay common is a separate terminal, whereas on the new Hive presumably...
I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.