you don,t state the distance from the 3phase db to your new cons.unit,personally i would,nt use less than 10/16mm plus additional earth.
yours benji
approx 5 meters at the most.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Need quick help with IT room in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
you don,t state the distance from the 3phase db to your new cons.unit,personally i would,nt use less than 10/16mm plus additional earth.
yours benji
the 20amp sub-main will deffo be undersized
yeah i agree now that its been mentioned computers use a lot more power than what i originally thought. I had based the 20A on 10 machines running 300W each.
TBH i think im going to just run a 32A ring main. Its all in trunking anyway and it saves fussing about
However im still wishing to learn and understand so if I were to run a submain in 6mm fed by a 32A MCB to a small CU with 3x 16A RCBO type B would that have been OK??