Hi all,
Customer reports sporadic nuisance tripping of RCD. I cannot reproduce it, or fault anything, except SOMETIMES on EFLI test it trips the RCD (megger mft 1553 'no trip' test).
I'm out of ideas here, can anyone help? This is what I've got:
- TT installation (small domestic);
- 30mA RCCB main switch incomer (Crabtree starbreaker);
- all circuits IR test 8MOhm to L&N-earth;
- RCD testing off load and on load all fine, ramp test 23mA off load 19mA with everything on.
- Ze about 160 ohms down the rod, drops to 12 ohms with all bonding connected.
 
Might need a leakage tester because combined leakage of the circuits maybe occasionally tipping it over the edge which is what your tester maybe doing.
Ramp test with everything on and running 19mA - I've tested loads of RCDs on load like this and never has one tripped out.
I agree the most likely cause at the moment is combined leakage when something starts up, I just haven't been able to reproduce it.
She also says the RCD was 'tripped' after a power cut - I guess indicating that the startup leakage of everything together was >23mA when the power came back in again. But.... I cannot reproduce that either.
 

Reply to Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top