Hi all,
Customer reports sporadic nuisance tripping of RCD. I cannot reproduce it, or fault anything, except SOMETIMES on EFLI test it trips the RCD (megger mft 1553 'no trip' test).
I'm out of ideas here, can anyone help? This is what I've got:
- TT installation (small domestic);
- 30mA RCCB main switch incomer (Crabtree starbreaker);
- all circuits IR test 8MOhm to L&N-earth;
- RCD testing off load and on load all fine, ramp test 23mA off load 19mA with everything on.
- Ze about 160 ohms down the rod, drops to 12 ohms with all bonding connected.
Might need a leakage tester because combined leakage of the circuits maybe occasionally tipping it over the edge which is what your tester maybe doing.
Ramp test with everything on and running 19mA - I've tested loads of RCDs on load like this and never has one tripped out.
I agree the most likely cause at the moment is combined leakage when something starts up, I just haven't been able to reproduce it.
She also says the RCD was 'tripped' after a power cut - I guess indicating that the startup leakage of everything together was >23mA when the power came back in again. But.... I cannot reproduce that either.
Reply to Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...