Hi all,
Customer reports sporadic nuisance tripping of RCD. I cannot reproduce it, or fault anything, except SOMETIMES on EFLI test it trips the RCD (megger mft 1553 'no trip' test).
I'm out of ideas here, can anyone help? This is what I've got:
- TT installation (small domestic);
- 30mA RCCB main switch incomer (Crabtree starbreaker);
- all circuits IR test 8MOhm to L&N-earth;
- RCD testing off load and on load all fine, ramp test 23mA off load 19mA with everything on.
- Ze about 160 ohms down the rod, drops to 12 ohms with all bonding connected.