Although not a requirement, I would also conduct a line test to make sure L&N also return a low enough measurement to satisfy disconnection times. An RCD would not detect such a fault.RCBO means you only need to comply with the requirements for RCD Zs however I’d check that earth leakage isn’t going to be an issue if the extended circuit will be used for PC’s