Hello, I was doing a job today connecting up the SWA I've put in to supply the electric gates. The DB is a three phase connected up as single phase. They have taken the 25 MM into the L1 of the 3 pole Main switch but the neutral goes straight to the N bar. Its a PME system. Am I right to say that it should isolate both L+N or is it expectable how it has been done?
 
I think the regulations state that for a TNCS / TNS system it is not necessary to isolate the neutral but then goes on to say that for installations not under the control of skilled or instructed persons that the neutral should be switched. (but I could have remembered wrong!)
 
If this is domestic or similar set-up where the switch may be operated by an ordinary person then 537.1.4 will apply and both live conductors of the single phase supply.

537.1.2. Quoted above has 2 exceptions highlighted of which the OP may be subject to but we lack info'.
 

Reply to Need to switch neutral for single phase domestic DB in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
988

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top