Hello all,

I did some per inspections at my next job and found that the customer had no cpc at some points in the lighting circui, I then looked further around the other circuits and noticed the upstairs power circuit looked a little strange. At each SO there was only 1 cable so I assume someone has run a JB under the floor and then took various supplies from this point to feed all socket outlets. My question Is can I just reduce mcb to 20amp and class as a radial or is it a re-wire. The circuits with no cpc will be re-wired without question.

Cheers in advance for any advice you can offer.
 
is it an old system? in the olden days sparks installed "jamaican ringmains" under the floor, basically it was a ring and a JB added everywhere where a socket was needed and a short spur from the JB to the socket, every socket in the house had one wire in it but there was a ring under the floor, before you ask, I have no idea why it is Called a Jamaican ring main.
 
Stupid question, but how many lines go to the MCB/fuse?

If 1 it's a radial, if 2 it's either 2 radials or a ring so a continuity test will tell the story.
 
yes , you can de-rate the circuit to 20amps if you feel thats best.
how many legs / feeds at the mcb ?
if theres 2 with end to end continuity , then its still a ring even if wierdly connected at the sockets.
 
Last edited by a moderator:
It's fairly evident that were are going to be JBs under the floor and clearly they won't be MF.

What code would that be getting? 3?
 
So would you all suggest a re-wire is the right way forward as JB's under the floor dont conform to regs...........however the work I am doing relates to completely different cirrcuits........so assuming that work is correct, how far do you go?.
 
So would you all suggest a re-wire is the right way forward as JB's under the floor dont conform to regs...........however the work I am doing relates to completely different cirrcuits........so assuming that work is correct, how far do you go?.

if your readings are OK, then leave as is. this method was used some years ago to save a few quid on cable. ( when a drum of 2.5mm was about a fiver ). considering the current price of cable, it's time it came back.
 

Reply to Neither a ring nor radial! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
224
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Not sure what you mean by pre-IP? as IP guidance was introduced long before 12v halogen downlights became 'fashionable'. That aside I would ditch...
Replies
2
Views
282
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top