measured 240 v on neutral to earth when disconnected neutral leg off light circuit
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss neutral 240 v in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If you disconnect the neutral of a lighting circuit from the cu when the power is still on, then the current will flow through the lamps and the neutral will equal the same potential as the live side.
totally wrong!!!!! there is NO current flow, therefore zero volt drop. that's why you get the 240V on the disconnected neutral
measured 240 v on neutral to earth when disconnected neutral leg off light circuit
measured 240 v on neutral to earth when disconnected neutral leg off light circuit