measured 240 v on neutral to earth when disconnected neutral leg off light circuit
 
What circuit were you actually measuring when you disconnected the light circuit? ....... sorry for the vague response but the question was vague so Im narrowing down options!
 
Best turn the lights off, that might help or you could knock the breaker off for the lights. Grabbing hold of the neutral whilst standing on a step ladder with a coffee in your hand is NOT recommended.
 
If you disconnect the neutral of a lighting circuit from the cu when the power is still on, then the current will flow through the lamps and the neutral will equal the same potential as the live side.
 
If you disconnect the neutral of a lighting circuit from the cu when the power is still on, then the current will flow through the lamps and the neutral will equal the same potential as the live side.

totally wrong!!!!! there is NO current flow, therefore zero volt drop. that's why you get the 240V on the disconnected neutral
 
Thats what i was trying to get across, if you do not touch it then there will be no volt drop, but if you do touch it then big volt drop.
 

Reply to neutral 240 v in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K
Hi Mike, Floating Neutral. I'm really over simplifying below, but using generators as an analogy is possibly easier to understand. In a large 3...
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top