M

mikex79

HI
Doing a test with a voltage detector/continuity tester on live PME/TN-C-S system installation at a socket outlet either with load and without the load shows voltage between live and neutral and live and earth but live-earth seems to be short circuited and the continuity tester indicates continuity which for me means thet they are short circuited (and I recon they are short circuited ot the orgin as the system gets only one PEN conductorfrom the supplyer which acts as a neutral and CPC at the same time) but the probelem is that even if I switch off the MCB which seems to be very old type like from 20-30 years ago nothinch changes and the continuity between earth and neutral still exist. my question is if it is cused becouse the mcb may not be a double pole switch? if it safe (all appliances connected to the sockets work propelly but the question is if they are safe)? what test should i do on top of what i have dont to make sure all of above?
many thanks
 
Last edited by a moderator:
You need to ensure main switch is off before carrying out any of the tests you describe.

You could try an IR test between all conductors and it should read clear, with the main switch off, all mcb's off.
 
You need to ensure main switch is off before carrying out any of the tests you describe.

You could try an IR test between all conductors and it should read clear, with the main switch off, all mcb's off.
disconnect neutral from the cu or both neutral and cpc you will find it will clear
if not you have a problem
 
You need to ensure main switch is off before carrying out any of the tests you describe.

You could try an IR test between all conductors and it should read clear, with the main switch off, all mcb's off.


shall I disconnect the CPC and neutral conductors before I do an insulation test?

You need to ensure main switch is off before carrying out any of the tests you describe.

You could try an IR test between all conductors and it should read clear, with the main switch off, all mcb's off.


shall I disconnect the CPC and neutral conductors from the cosumer unit before I do an insulation test?
 
Last edited by a moderator:

Reply to Neutral CPC short circuited in PME system, is that correct? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
442
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top