neutral earth continuity | on ElectriciansForums
Discuss neutral earth continuity in the Australia area at ElectriciansForums.net
sparks1653
Hi everyone. i was helping/learning on a job today where the company was installing a new 3 phase distribution board in a shop. they isolated the incoming cable (incomer had an isolating switch as was a submain) and installed the new board. i was being shown how to test it and got some readings i saw that i dont understand.
with supply dead there was continuity between earth and neutral, and also got 0.00 on an insulation resistance reading between neutral and earth. could someone explain this to me please?
If the installation is TN-C-S, the earth and neutral are linked.
As Tony has said, if the neutral is not disconnected by the main switch, you will have continuity, unless you disconnect either the main earth or the neutral.
You should not really be conducting an IR test between conductors that have continuity.
You an also have continuity between earth and neutral on TN-S installations, as often the rest of the network may be TN-C-S, and continuty may be via another installation.
Reply to neutral earth continuity in the Australia area at ElectriciansForums.net
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.