Did a CU change recently, replacing a Wylex rewirable.
Gobsmacked to find 3 sockets in one room on the ring with Earth and Neutral swopped.
I suspected something amiss from the results of my initial L+N to E IR test when lots of things were still plugged in.
The L/N or L/E cross-connection continuity test at each socket will reveal this fault, and must be done.
On radial circuits, an R1 + R2 test at each socket will reveal this fault.
However, on powering up I like to do a quick check of every socket with a socket tester.
My socket tester doesn't register this fault. Is there a reasonably priced one on the market which does?