Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket tester. | on ElectriciansForums

Discuss Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket tester. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Piratepete

Did a CU change recently, replacing a Wylex rewirable.

Gobsmacked to find 3 sockets in one room on the ring with Earth and Neutral swopped.

I suspected something amiss from the results of my initial L+N to E IR test when lots of things were still plugged in.

The L/N or L/E cross-connection continuity test at each socket will reveal this fault, and must be done.

On radial circuits, an R1 + R2 test at each socket will reveal this fault.

However, on powering up I like to do a quick check of every socket with a socket tester.

My socket tester doesn't register this fault. Is there a reasonably priced one on the market which does?

Cheers
 
Re: Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket test

My socket tester doesn't register this fault. Is there a reasonably priced one on the market which does?

Cheers

Of course not... neutral is bonded to earth at the tranformer. In a TNCS system they're connected in the cut out - for all intensive purposes they are the same conductor at the same potential
 
Re: Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket test

Of course not... neutral is bonded to earth at the tranformer. In a TNCS system they're connected in the cut out - for all intensive purposes they are the same conductor at the same potential

Ok! I just thought that there might be one with clever electronics that could spot the difference. My MFT trips the RCD with a loop test on a faultily wired socket but it's hardly appropriate for a quick check!:uhoh2:
 
Re: Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket test

Yup, see that all the time. I had a light fitting a while ago where all the neutrals were in the earth terminal in the ceiling rose and the cpc was in the neutral. The wonders of DIY huh?
 

Reply to Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket tester. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top