One_of_them
guys,
head is battered its been a bad day and cant think straight.
Replaced a 3kW water heater element and everything went well. Circuit tested out fine so turned everything back on but when the element is pulling im getting L-N 238 L-N 234 N-E 4V!!! This was tested at element but is the same at the supply side of the 13A DP FCU but at the board (3phase) N-E is nothing (well mV anyway) When element or FCU is off everything is normal
I have checked all relative connections and even checked another heater on site and it is the same.
Is this just the way elements are?
Why would the supply side of FCU have 4V but the board not?
cheers all have a good weekend and some lovely cold beers
Welcome to the world of volt drop. You get VD* in the neutral as well as the line. Hence the 4V between N and E at the load.
(Deleted a load of waffle)
*(Sounds like a trip to the clap clinic is due).
But the following figures and the drawing are right
The 4v is probably just voltdrop on the neutral as Tony mentioned.It might be worth doing a visual earthing check and an earth impedance test, if the earthing is tn c s it's a little higher than I'd expect to see.
unless your a BG engineer!! 4v is deadly and they need to upgrade all your earth and bonds and remove your split load box and install a dual rcd.... not to mention replace your boiler and pipework!!
all because his volt stick LIT up...!!
Its not Induced voltage. Its VD.
Doesn't matter what earthing system it is, If you'v got VD, you'v got VD mate!!!
It'l be same on any system.
You get VD under load conditions. Its normal and nothing to worry about. It shouldn't be more than 5% for an immersion heater.
i might be having a blonde moment here. understand there is probably a bit of a VD under load, say there's a VD of 4V L/N. why is that not 4V L/E as both N and E are assumed to be 0V. so therefore 0V N/E?
There’s volt drop along the neutral. At the source (the CU) N and E should be more or less equal. At the point of load there will be a slight rise between N and E. 4V will give a total of 8V for the entire L/N loop. Which equals 3.47% volt drop, perfectly reasonable.
If the current is high enough that the l and n wires become part of the load and an equal voltage would be dropped across each. At the immersion heater you could get a 4 volt reading between n and e but the closer you get to the n-e bonding point on tncs the n-e voltage should get less. I actually misread part of the OP where he says he measured 4v at the FCU. I thought he was talking about the CU. All the terms like FCU and CU are not used here so occasionally I translate incorrectly so the blonde moment is at his end not yours :(
thanks for that, tony. i'm just trying to get my head round it. i see why, but not how, if yo know what i mean. :28:
guys,
I think what you mean is that
L-N voltage is 234V
L-E Voltage is 238V and
N-E Voltage is 4V
Quite normal.
telectrix:-
Volt drop in the neutral wire when under load, therefore Neutral voltage at load end relative to MET = 4V
No voltdrop in earth wire as no current flow in it, Therefore CPC voltage at load relative to MET = 0V,
therefore N-E = 4V
Reply to neutral-earth voltage in the UK Electrical Forum area at ElectriciansForums.net
If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Could be damage to the N core touching the fabric of the building but the CPC of that cable is insulated from both. I.E. a screw clipping the edge...