guys,

head is battered its been a bad day and cant think straight.

Replaced a 3kW water heater element and everything went well. Circuit tested out fine so turned everything back on but when the element is pulling im getting L-N 238 L-N 234 N-E 4V!!! This was tested at element but is the same at the supply side of the 13A DP FCU but at the board (3phase) N-E is nothing (well mV anyway) When element or FCU is off everything is normal

I have checked all relative connections and even checked another heater on site and it is the same.

Is this just the way elements are?
Why would the supply side of FCU have 4V but the board not?

cheers all have a good weekend and some lovely cold beers
 
If you think of the N cable as having some resistance (as will the L conductor).

it will be possible to pull the N conductor at the end nearest the load towards the load (supply) slightly (raising it by 4V in this case) as it (the N conductor) has a slight VD along it's length, which is proportional to the current it is passing.

the E conductor meanwhile has no load on it, as it is not passing any current, hence the slight discrepancy.

Tony may be able to post the vector/phasor drawings better than I can.


Surely if you pull the N conductor it will stretch and get thinner and increase its resistance and all your maths will be wrong and to be done again.
 
And there was I, believing my old lecturer when he taught us it was all about electron-hole-pair movement....

What are you saying now, we have to fit the non-existent electrons in to Holes now?
This is just silly and a farce!!!!
How can you put something into a hole when you can't see it in the first place.:flowers:
 
Last edited by a moderator:

Reply to neutral-earth voltage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K
  • Question
Could be damage to the N core touching the fabric of the building but the CPC of that cable is insulated from both. I.E. a screw clipping the edge...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top