Hi guys,
been to a fault today where customer is saying they have no power to 6 sockets but all other points ok (all power on one ring main)
when I arrived I checked for power with my martindale and got a L-E reverse symbol at the six points. I then checked voltage at the sockets and got 230v L-E and N-E but nothing L-N. So I thought I must have a neutral fault somewhere.
i then checked ring continuity and found the neutral open circuit. Why would it show voltage across my neutral to earth when all loads have being disconnected. I have checked all sockets and cannot find a loose connection. Any advice on where to go next. If you have any questions where I have not made myself clear just ask. Thanks
 
any plumbing been done recently? i ask because the other week i had the same fault. the wet-pants had put his circular saw through a 2.5mm. cut clean through the neutral. sod must have known he'd done it as his saw would have stopped. bugger fitted his pipes, nailed the boards back, said nowt. lucky i was in a good mood that day or i'd have nailed his pipes.
Is geordie back on his feet? :biggrin:
 
Cut the nonsence regarding continuity checks and whack 500 volts between all cores as you were trained on site and at tech when you did your apprenticeship, it is the only way to check all is okay, 1000 even, any problems will show straight up.
how will an IR test show a broken conductor?
 
If it's a ring then all the sockets will have voltage regardless of a break in the rn. You need to check whether you have correct r1 and r2 to verify the circuit is actually wired as a ring,it sounds like it isnt. If r1 and r2 are good then that would suggest more than one break in rn.
 
how will an IR test show a broken conductor?
meggar between the neutrals at the board, if there is a break in the ring it will show up, if there is a short between neutral and earth it will show up, I would meggar the cores and then do a r1+r2 as well afterwards, anytime there is a fault on a power circuit I would meggar all the cores to see if any breaks or shorts evident.
 
Should have said that I did an IR test and it showed 0.02 meg across one leg of neutral-E (no RCD fitted,no PME just some more info I missed sorry guys)everything else tested ok so I know there is a problem,I will start breaking circuit down tomorrow. No plumbing being done or DIY work.
 
Should have said that I did an IR test and it showed 0.02 meg across one leg of neutral-E (no RCD fitted,no PME just some more info I missed sorry guys)everything else tested ok so I know there is a problem,I will start breaking circuit down tomorrow. No plumbing being done or DIY work.
Fair enough mate, I would have also done the same test.
 
meggar between the neutrals at the board, if there is a break in the ring it will show up, if there is a short between neutral and earth it will show up, I would meggar the cores and then do a r1+r2 as well afterwards, anytime there is a fault on a power circuit I would meggar all the cores to see if any breaks or shorts evident.

Buggar that,do an insulation test instead.
 

Reply to Neutral fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Very technical :D
    • Like
Replies
9
Views
517
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top