Hi guys got a IR fault, basically there is a low IR reading on the upstairs sockets Live to neutral nothing strange there, but the rcd will only trip if the lights are switched on. so this is what happens i disconnect the lights and the upstairs sockets work rcd does not trip, then connect the lights still ok then flick any light switch and rcd trips. Disconnect the upstairs socket neutrals and everthing else works fine. Iam going to split the ring to find the fault but why would it affect the lights, is it an earth fault? any ideas guys? cheers i know you will want questions answering so ill do my best.
 
0.9 Megs is borderline for most RCD's, tripping might only occur when there's a decent current flowing through it hence the tripping when the lights are switched on. I would just trace the fault in the normal way, identify the circuit, make sure it's not crossed or borrowed to another circuit then start splitting it up into sections.
 
Thanks for the replies guys, i was leaning toward the earth fault when i was there i mean its an easy enough fix if i just split the upstairs ring and narrow down the fault and isolate it, that would probably solve the problem , but the lights are affected too and its narrowing down that fault which will require more investigation. But you know people they are just happy as long as the leccy is on. The problem is there is the meter which feeds a 80a RCD which then feeds 4 consumer units all old wylex fuse boxs, but the lights fuse box is located in a different place from all the other boxs. its a real mess of a wiring job, which makes my job that little bit harder, why dont people want PIRs done on new builds when the wiring has never been touched LOL. I hate the amount of times sparkys in the past have just added new fuseboxs or rcds of other circuits or straight from the mains and you then end up with loads of boards and switches and rcds all doing different jobs instead of just updating the consumer unit and keeping it simple.
 
. I hate the amount of times sparkys in the past have just added new fuseboxs or rcds of other circuits or straight from the mains and you then end up with loads of boards and switches and rcds all doing different jobs instead of just updating the consumer unit and keeping it simple.

and never a diagram or explanation or results for the poor bugger who has to follow lol!
 

Reply to Neutral insulation fault strange! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
131
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
914
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Oh dear, I missed the date!!!
Replies
6
Views
667
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
965

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top