D

dmh

I've been investigating a problem today with an RCD that keeps tripping. I have discovered that on one of the ring circuits that is RCD protected there is a neutral connection to the non rcd side of things but for the life of me I cannot track down where it occurs. Any suggestions from anyone as to how to find this and is this likely to be the cause of the RCD tripping (customer is adamant that nothing has changed recently and the RCD problem has only just started happening)

Thanks
 
The shower is downstairs so not as though water is leaking through and down onto anything and I would say that its happening too quick for it to be water leaking somewhere it shouldn't. Turn shower on, turn kettle on and it trips. Incidently kettle on it owns works fine or at least it seems to when i test it but customer has said that sometimes tripping does occur when shower not in use.
 
Might be worth trying to get customer to keep a log of what appliances are on when the rcd trips - you could be in the unlucky position of having more than one cause. Anything with electronics washing machine , microwave etc etc could be contributing.
[ you sure the sockets ring isn't running nearby in the wall , clutching at straws with the water leaking]

Edit : just a quick check - we are talking electric shower and not a power shower aren't we?

Edit again : have you tried ramp testing the rcd?
 
Last edited by a moderator:
You say you have linked between the neutral on the side with the RCD and the other side but if you do each circuit individually you may get a better understanding, ie a borrowed neutral for a lighting circuit perhaps. Once you know which 2 circuit neutrals are connected you can wanderlead across the 2 circuits to track down the problem.

It takes a while, had a nicked neutral cable touching the backbox last week (causing a short between earth and neutral). When I pulled the sockets I couldn't find the fault. Took bloody ages to work out what was going on, and no it wasn't me that nicked it!!
 
Good idea to ramp test the RCD. It may just be that. As noted in a previous post quite a lot of modern appliances have High Earth currents and you could be leaking a few from TV. computers. Washing machines etc, a 30Ma RCD will most likely trip in the late 20Ma but if the RCD is old or somehow not quite up to standard it might be tripping a lot lower, perhaps below 20Ma. A ramp test will tell you what it is tripping at.
 
Don't know if this will help but had a similar problem few years back. Rcd tripping intermittently, but only when load reached a certain level. Thought it was kettle at first but if you ran it with everything else ie TV, video etc unplugged it wouldn't trip. Add say the TV & vid back into equation, off it would go. Eventually traced to a spur from the ring that ran under the carpet between the skirting and the carpet gripper, not a great idea in the first place but even worse when the cable runs across the gripper which has lots of little pins sticking out of it. Turned the cable over and there were loads of indentations/punctures in the mechcanical protection. A very small amount of current must of been leaking via the gripper but only activated the rcd when the load on that circuit reached a certain level. Re-wired the spur properly, problem sorted.
 

Reply to the thread, titled "Neutral Inter Connections" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top