Having an issue with some downlights. The lights suddenly stopped working and the customer said they had no idea why! The downlights are on a downstairs ring and none of the other lights are effected. So my first thought was a problem with one of the transformers so I disconnected each transformer in turn to see if I could eliminate the one that was causing the problem (only three lights).
Removing each transformer didn't help so I disconnected the rest of the circuit from the first light so there was only one light being feed from the switch wire and fitted a new transformer. Again not working and when I tested the voltage before the transformer and it was only giving 50 volts, removed the transformer and downlight and tested it again and it gave 240 volts!

So whenever I put a demand on the circuit I lose masses of voltage... so I can only think of a broken or badly terminated neutral as the reason??!! Access is a issue in trying to track this neutral down so could I link into another lights neutral from the same ring? No other rooms are affected so this seems a logical solution. I have access for this and I can't think of a reason why it wouldn't work??!!

Suggestion please. Very new and learning. Fine with installing new stuff but fault finding and problems solving I struggle with...

Thanks
 
Hi Daniel,
Its not good practise to feed lights from a ring main,not your doing but if possible it would be best to supply the
lights from the lighting breaker,if you link a lighting nuetral to the downlights you could cause
crossed nuetral to the ring which would trip any rcd.
 
If you start testing the circuit as if it were a new circuit, that should throw up some odd results somewhere along the way which will give you a good indication. Given that the problem is with the downlighters that will give you a starting point.
Try to avoid putting 500v across live and neutral though...
 
Yes that will be fine,sorry when you said downstairs ring i thought you meant ring main,
maybe its me but i refer to rings as ring mains and lights as lighting circuits.
you will be fine,sometimes its easier to run a new cable than trying to find
the fault,just remember to disconnect the original cable.
 
Again not working and when I tested the voltage before the transformer and it was only giving 50 volts, removed the transformer and downlight and tested it again and it gave 240 volts!

So whenever I put a demand on the circuit I lose masses of voltage... so I can only think of a broken or badly terminated neutral as the reason??!!

If you're measuring the voltage between line and neutral, why do you think that it's a neutral fault? Surely it could just as well be a fault in the line?
 
you could seperate section and do an an R1 R2 then an R2 Rn....see if the results are similar (assuming it is t&w)...what size cable is it? 1mm?....1.5....?....
 
Last edited by a moderator:
As a rule in most UK domestic installations you should always get zero volts if you test between neutral and earth (CPC). If you get a voltage (>1volt) between neutral and earth even when the circuit is live and under load then you have a neutral problem.

A drop in voltage (L-N) could indicate a missing or partially missing live or neutral.
 

Reply to Neutral issue me thinks!!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
689
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top