K
Kev2632
can a neutral to earth fault blow the rewireable fuses/ MCB?? when the load is applied to the neutral? is that at all possible??
... Why does a L to N trip the mcb or fuse??!" is it because of the potential difference??? ... /QUOTE]
I think the fact you ask this question, that you must have little electrical knowledge and therefore recommend that you employ the services of a qualified electrician. If you post your location I'm sure one of the local members on here will be able to help you.
Kev
In very early days, there was no standard for electricty supply. Some were DC, Some were AC, all were without an earth and therefore there was no neutral, just 2 lives (or a +ve and -ve), so they used to fuse both of them. When the supply was standardised, fuses only ever protected the live but some of the old fuse boards still exist. One of my would-be customers still has one. She says she is too old to think about upgrading and rewiring, and is happy to take the chance that her electric installation may shorten her remaining time in this world, against my advice.
If your fuse board has a wooden frame with shiny white porcelain fuse carriers behind a hinged wooden door/cover - often with a hook and eye catch, then you may indeed have fused neutrals and should get it professionally checked out. It could be quite expensive to sort this so be prepared for a large bill.
What exactly do you mean by "...And why would it only cause it to happen on a dead circuit? " I am thinking maybe you do have one of these old boards.
The fuse (MCB) can blow due to a L-N or a L-E fault.
2 possibilities come to mind:
1) You have a L-E fault somewhere else, with a poor (absent) or broken earth upstream. The neutral-earth fault passes the current of that L-E fault as the neutral becomes the earth, and it would appear that the N-E fault causes the fuse to blow. This would, however mean that some or all earths are live, but on a circuit of just plastic (dare I say porcelain) pendants and switches, this may not be immediately apparent. If you have a fused neutral, a L-E fault on any other circuit may cause the neutral fuse to blow even with the lighting live fuse removed. If you do have fused neutrals it's likely you have no incoming earth system but could well have lead sheathed waxed paper cables that would provide the earth continuity that would allow your symptoms to exist.
OR
2) A black or blue switch wire may be confused as being a neutral.
Reply to the thread, titled "neutral to earth fault blow rewireable fuse/mcb??" which is posted in Australia on Electricians Forums.