Hi folks,

so here was a new one I came across today. Was sent to put in a new bathroom fan today to an old Barrats house. Opened up the switch at the bathroom door to have a look - no neutrals. Ok I thought, neutrals obviously looped at the ceiling roses. Wanting to test the circuit first, I wanted to find out which neutral was feeding the circuit as they weren't in order. To cut a long story short, I removed every single neutral (bar the incomer) from the neutral bar, and the lights stayed on! After calling another spark, he recommends pulling the main earth and low and behold - the lights went off.

What are everyone's thoughts on this, and have you come across this before? Crossed neutral somewhere or have they used a cpc as a neutral somewhere along the line?

The house had an octopus box for the lights which I have never seen before, and never want to see again!

The fault was recorded on the test sheet and have advised that customer that they should have this looked at. A new feed was run to the bathroom light switch off of another lighting circuit through a local RCD. The faulty circuit is a shambles from the previous owner and have told the customer they may be quicker and cheaper having someone to quote for the affected rooms to be rewired.

Look forward to your responses.
 
Lifting the earth was a Very Bad Test (tm) for two reasons.

1: It's dangerous. Not only all the appliances and metalwork and everything in the house becomes live via the fault, but if there are any extraneous parts outside the house in contact with any circuit's CPC (water pipes connected via the boiler, shared service mains etc) then they could become live too and endanger someone in another property.

2: It's not guaranteed to give the right result: E.g. if the C/H system has metallic contact to an incoming water main your lighting load will still work, with the current returning to earth through the main. So you're no further forward with your testing. But a simple IR test would find it for certain, and without the danger.

IMHO it's like searching for a gas leak with a match.
 

Reply to Neutral to earth fault - lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
591
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
953
Very technical :D
    • Like
Replies
9
Views
565

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top