So since the advent of rcds, these have become more highlighted.
This has been bugging me lately. In my mind the reason why neutral to earth faults are a problem is because the cpc has a smaller csa than the neutral
Also if you lost the neutral at the supply then mains voltage would be present (minus load resistance's volt drop) at all exposed conductive parts. What other reasons are there? Thanks for help in advance.
Not quite sure which element of this you are not understanding but - in the event of a neutral to earth fault in a lighting circuit:
1) The returning current (neutral) of all other circuits in your installation now have an alternate path to return to the supply (through the earthing system). At the neutral bar most current will return through the main neutral but some will return through your N-E fault path. The level of current through your fault will be determined by its resistance compared to that of the ‘normal’ route - this current can be high enough to overload those 1.5/1.0mm cables. Most often the resistance of your fault path is high enough to prevent excessive current so the fault can go undetected for years (assuming not protected by RCD)
2) If, in addition to the N-E fault, you lose your supply neutral then your fault will be the
only route of return and the 1.5/1.0mm cables will attempt to carry
all the neutral current of your installation - obviously this will seriously overload the cables and could result in fire. Lost supply neutrals are not common but can happen particularly with overhead supplies - also a lost supply neutral can occur in your
own consumer unit by loose connection (come across this a number of times).
3) As Darkwood mentioned you can also have floating voltages present - eg if TN-C-S supply then a lost neutral will mean also a lost earth so returning current will have nowhere to go, resulting in potential difference between exposed conductive parts and GM of earth - though this will likely be reduced by main bonding connections.
Note: I have only just got up and haven’t had my porridge yet so all of the above could be absolute sh1te
- if anyone wants to correct/add anything, feel free!