Been to look at a faulty socket on a rcbo and wont hold in, tried to test trip times etc but reading voltage on earth. Supply is tt, 3ph and 1 ph to a domestic property. Shared earth rod. Cant turn house off as belongs to separate person. So tested voltage at 3 ph db, 230, 400 v etc but got 48v n to e.. so i did insulation test on incoming swa, phase to earth, one down to 350 ohms, n to phase, one 459 ohms, n to e grater than 500 ohms. But can work out why 48v n to earth. House looks to have split load rcds, looking through window. My only conclusions is swa supplying house has low insulation. Am i looking in wrong direction. Ive turned power off to barn till i can look at house supply.
 
A loose neutral connection would not affect the voltage at the MET with respect to real earth. It would also have caused incorrect voltages L-N and L-L which the OP says were OK at the time when there was excess voltage N-E. So I think that's a red herring.

There was a test result for Zpn (not 'L-N ze' that doesn't make sense!) of 0.4ohms, which is plausible, but the MFT couldn't test Ze. As the installation is TT that suggests the rod is completely hopeless and a small amount of leakage (possibly a perfectly normal amount) from equipment in the house is enough to raise the voltage drastically. Nothing terribly surprising there.
 
Last edited:
We have one of two things going on here;
Either the earth rod is high resistance and thus not working and needs fixing, or there is a L-E fault that is putting AMPS down that earth rod. In both cases there is a fault that needs fixing so the installtion in the first case is properly earthed and in the second case prevent fire and the electricity meter going round like a cathrine wheel!

Go back to the customer and explain that if this leak was gas, would they stop you from fixing it? If the property is rented then they have a duty of care and you may also find suitable phrases in the Electricty at work at.
 

Reply to neutral to earth high voltage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top