Doing a favour for a friend and using it as a learning experience as well.
Guy is going into a new unit with an existing 1ph board. he has a 3ph machine so wants to upgrade mains etc. New board will supply everything in the small industrial unit from heating/lights through kitchen sockets.
I've done the calcs for A/phase etc but then started thinking about what equipment to specify. Most boards come with a main switch included and an option to upgrade to RCD incomer. However with this you get no diversity to circuits. So I was thinking that any new install has to have a c type 100mA rcd incomer with b type 30mA rcbos to any single phase circuit on the board................. Or am i just complicating things?

Many thanks in advance for the advice.

Tony
 
Use a standard incoming isolator. The 3ph loads can be fed via 3 pole MCB’s, where as the single-phase loads via RCBO’s.

You could fit a type S RCD to cover the entire board. But you have to weigh up the pro’s and con’s of the situation
 
the discrimination rule of x3 for RCD's only works ifthe fault curent is near the nominal I delta n of the closest device. much more than that and you dont acheive discrimination. This is why nowadays'its more common to use S-types as Tony has said. Definately fit a normal mains switch.
 
Doing a favour for a friend and using it as a learning experience as well.
Guy is going into a new unit with an existing 1ph board. he has a 3ph machine so wants to upgrade mains etc. New board will supply everything in the small industrial unit from heating/lights through kitchen sockets.
I've done the calcs for A/phase etc but then started thinking about what equipment to specify. Most boards come with a main switch included and an option to upgrade to RCD incomer. However with this you get no diversity to circuits. So I was thinking that any new install has to have a c type 100mA rcd incomer with b type 30mA rcbos to any single phase circuit on the board................. Or am i just complicating things?

Many thanks in advance for the advice.

Tony


And what happens if you develop a neutral fault?
 
You probably don’t notice it. There must be 1000,s upon 1000’s of boards through out industry without E/L protection. It's the exception not the rule to fit them.
 
I agree with those that have stated to leave the main switch as a 4 pole isolator. As for choices as to what type of breakers you install, that would very much depend on what that breaker is supplying. A b type breaker may be of no use at all, on some machinery with high in-rush currents, be they 3 phase or single phase. You need to match the breaker type, to the type of load it's feeding. This could mean a mixture of B's, C's and even D's in your DB.

Any circuits requiring RCD device protection, can be accommodated with either RCBO's for single phase, or Vigi type units, for single or multi phase circuits.

When working on Industrial and to some extent Commercial installations, you have to forget about your usual domestic CU set-ups. In the main they will be somewhat/completely different, both in make-up, and in the type of loads they will be supplying....
 

Reply to New 3 phase installation in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
527
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
660
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks