Tony Way

-
Arms
Doing a favour for a friend and using it as a learning experience as well.
Guy is going into a new unit with an existing 1ph board. he has a 3ph machine so wants to upgrade mains etc. New board will supply everything in the small industrial unit from heating/lights through kitchen sockets.
I've done the calcs for A/phase etc but then started thinking about what equipment to specify. Most boards come with a main switch included and an option to upgrade to RCD incomer. However with this you get no diversity to circuits. So I was thinking that any new install has to have a c type 100mA rcd incomer with b type 30mA rcbos to any single phase circuit on the board................. Or am i just complicating things?

Many thanks in advance for the advice.

Tony
 
Use a standard incoming isolator. The 3ph loads can be fed via 3 pole MCB’s, where as the single-phase loads via RCBO’s.

You could fit a type S RCD to cover the entire board. But you have to weigh up the pro’s and con’s of the situation
 
the discrimination rule of x3 for RCD's only works ifthe fault curent is near the nominal I delta n of the closest device. much more than that and you dont acheive discrimination. This is why nowadays'its more common to use S-types as Tony has said. Definately fit a normal mains switch.
 
Doing a favour for a friend and using it as a learning experience as well.
Guy is going into a new unit with an existing 1ph board. he has a 3ph machine so wants to upgrade mains etc. New board will supply everything in the small industrial unit from heating/lights through kitchen sockets.
I've done the calcs for A/phase etc but then started thinking about what equipment to specify. Most boards come with a main switch included and an option to upgrade to RCD incomer. However with this you get no diversity to circuits. So I was thinking that any new install has to have a c type 100mA rcd incomer with b type 30mA rcbos to any single phase circuit on the board................. Or am i just complicating things?

Many thanks in advance for the advice.

Tony


And what happens if you develop a neutral fault?
 
You probably don’t notice it. There must be 1000,s upon 1000’s of boards through out industry without E/L protection. It's the exception not the rule to fit them.
 
I agree with those that have stated to leave the main switch as a 4 pole isolator. As for choices as to what type of breakers you install, that would very much depend on what that breaker is supplying. A b type breaker may be of no use at all, on some machinery with high in-rush currents, be they 3 phase or single phase. You need to match the breaker type, to the type of load it's feeding. This could mean a mixture of B's, C's and even D's in your DB.

Any circuits requiring RCD device protection, can be accommodated with either RCBO's for single phase, or Vigi type units, for single or multi phase circuits.

When working on Industrial and to some extent Commercial installations, you have to forget about your usual domestic CU set-ups. In the main they will be somewhat/completely different, both in make-up, and in the type of loads they will be supplying....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Tony Way

Arms
-
Joined
Location
Cambridgshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
New 3 phase installation
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Tony Way,
Last reply from
Engineer54,
Replies
7
Views
1,770

Advert

Back
Top