Hi whats the situation on following!
went to wire a bathroom today in old terraced property all looked good new board (last 6 months) full niceic member! certificates not to hand YET! looked in loft to find V I R cables! works out from board new cables run 2 mtrs into joint boxes picking up old cables! as it happens its not a problem for me as found a pvc 6mm left in loft and other end just outside the board:))) so can work my stuff from this BUT i would only ever connect to old cable if we were doing a rewire very shortly after!! is this a Good Practice issue or is there a reg that said THOUT SHALL NOT CONNECT TO VIR even if it tests ok?? lighting hasnt cpc but thats not the issue as this has label on the board! diff subject the plumber used a junior hacksaw to cut through a live vir cable that just had no jb on end ASSUMING it was dead( he wont do it again:)
 
This forum. He asked if it was ok to pit VIR into a new board and the answer is ... YES. You're right about testing /making sure the cables are suitable for continued use but we ll know that! Does anybody reading this not know that the cables should be suitable?

How can you expect me to know? .. I'm just a plumber. :)
 
If you look in the online guide to Part P, you'll find somewhere at the back it makes a specific recommendation that VIR should be taken out of service as most of it has long expired. From a personal angle, I can't remember the last time I found some that was still in a safe usable condition - in fact the last near-miss house fire that I prevented was perished VIR shorting out and no proper ADS protection working. I've got some customers at the moment that we're slowly rewiring on a room by room kind of basis away from VIR to PVC (just to minimise disruption) - the board change will be happening last (they're on a 100mA already for a TT).
Ha! Part P, because I know how much you guys respect Part P.
 
This forum. He asked if it was ok to pit VIR into a new board and the answer is ... YES. You're right about testing /making sure the cables are suitable for continued use but we ll know that! Does anybody reading this not know that the cables should be suitable?

Well you're just not understanding that we disagree then. With any T+E my answer would be yes, unless proved not fit for purpose. With VIR my answer is no, unless it can be proved it is fit for purpose, which won't be possible.
 
Ha! Part P, because I know how much you guys respect Part P.

We don't. But as far as the OP and this thread is concerned, it's useful to know that there is actually some formal documentation that can be referred to for a customers purpose. It also has a section that discusses VOELCB's as well which is also useful to wave at a customer.
 
We don't. But as far as the OP and this thread is concerned, it's useful to know that there is actually some formal documentation that can be referred to for a customers purpose. It also has a section that discusses VOELCB's as well which is also useful to wave at a customer.
'Formal documentation' produced by a group most people on here call scammers
 
Well you're just not understanding that we disagree then. With any T+E my answer would be yes, unless proved not fit for purpose. With VIR my answer is no, unless it can be proved it is fit for purpose, which won't be possible.
I don't think we are disagreeing actully, but whatever; peace love and respect
 
I put a new board on for my mate's mother in law just before Christmas.

All VIR, 63 years old, told her that it needed a rewire but she took the attitude that she was 85 (I think) and that she didn't want it done.

All tested at 3-5 Mohm, so was left alone. She is aware that she may get issues with the rcd tripping at a later time, and is well aware that the house needs a rewire but isn't interested.

On the upside, I discovered a melted cable (PVC from an extension of the kitchen ring) that had near enough completely burnt through, in a bit of trunking behind a unit, worst thing was, it had been taped up 10 years or so back and just left to deteriorate


aru7ajy9.jpg

y4avepab.jpg
 
I would say about 20-30% of the VIR in my vintage cable stock was usable when it was removed and remains so now. One lot of 7/.029 that I only took out earlier this year is impressively tough - you can bend, flex, scrape, rub or bash it and it will probably outlast equivalent new LSZH singles. The ends are OK, not as good as the bits that have been deep within the conduit all their life. The insulation performance is as good or better than PVC (In fact at first rubber was usually better than equivalent PVC which was seen as a cheap inferior substitute). Other samples of VIR are so perished they are effectively bare wires. So in my experience, although it is a minefield, enough of a minefield that one should be avoiding keeping VIR in service if practical, it isn't a foregone conclusion that all VIR is inherently unusable in 2014. I maintain a couple of installs containing VIR about which I have no specific qualms.

FWIW I am about to take my car in for an MOT. The tester is not allowed to fail it just because many other cars of its age are rustbuckets. He is obliged to look at my own car and take it on its merits.
 
Once again,a contentious issue,where the only definitive statement would be to say the final say-so on continued use of the cable concerned,would rest with the person who inspected and tested it. I have found VIR in use,and,in good condition. Admittedly,this would invariably be where variations in temperature were limited,such as in a sub-floor. There are parts of this countries railways,water,gas and sewage infrastructure,functioning well with components in daily use,up to 100 years+ in age. Recently i removed some macerator and pump units from a cess pit as part of an upgrade to digester. These were 60 years old +,had never been removed,and were still working fine...all that P-Bronze hidden in gloop...:stooge_curly:
 
VIR if not stressed isn’t a problem, the installation method may be.

We were replacing two Metropolitan Vickers open slate panels with new MCC’s. The panels and cabling were installed in 1932. Samples of the VIR were sent to BASEC to see if it was suitable for continued service. Of the 250+ motors only a dozen or so needed re-cabling. The plant is still running to this day.

Testing the cables the minimum IR wasn’t set at the stupid IET one size fits all 1MΩ. We calculated the minimum insulation resistance by using the proper method where leakage current is not to exceed 1/10,000[SUP]th[/SUP] of the circuit FLC.
To be on the safe side we lowered the maximum leakage to 1/5,000[SUP]th[/SUP] at 2X working voltage. I.E. 1000V Ph→Ph, 500V Ph→E.


You can only go by observation and testing. NOT some myth that VIR will fall apart the moment you look at it.
 
VIR if not stressed isn’t a problem, the installation method may be.

We were replacing two Metropolitan Vickers open slate panels with new MCC’s. The panels and cabling were installed in 1932. Samples of the VIR were sent to BASEC to see if it was suitable for continued service. Of the 250+ motors only a dozen or so needed re-cabling. The plant is still running to this day.

Testing the cables the minimum IR wasn’t set at the stupid IET one size fits all 1MΩ. We calculated the minimum insulation resistance by using the proper method where leakage current is not to exceed 1/10,000[SUP]th[/SUP] of the circuit FLC.
To be on the safe side we lowered the maximum leakage to 1/5,000[SUP]th[/SUP] at 2X working voltage. I.E. 1000V Ph→Ph, 500V Ph→E.


You can only go by observation and testing. NOT some myth that VIR will fall apart the moment you look at it.

Well said, that Man....lol!!
 
We have lots of vulcanised rubber in our factory connected up to fancy flush brushed chrome accessories, management won't pay for a rewire, but will pay to replace light switches, light fittings etc, we make our recommendations get over ruled shrug shoulders and accept management knows best.
 
We have lots of vulcanised rubber in our factory connected up to fancy flush brushed chrome accessories, management won't pay for a rewire, but will pay to replace light switches, light fittings etc, we make our recommendations get over ruled shrug shoulders and accept management knows best.

Best way ... then you can laugh your wotsits off at them when it all goes to rat****.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New board connected to V I R cables
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
56
Unsolved
--

Advert

Thread statistics

Created
powervan,
Last reply from
Geordie Spark,
Replies
56
Views
11,303

Advert

Back
Top