posts #13 and #14 show totally conflicting info. no wonder OP is confused.com.
 
So troubled, I rang NHBC to enquire about their amendment of guidance in 2016, i.e. why & where from? They said it was more realistic, and from consultation with their members and partners?

I also rang Elecsa, who said it was still 300mm yada yada. I've emailed Electrical Safety First, to see if they can sink this one with a counter work top argument.

I've had a bit of a boring day :)
 
Last edited:
I'd probably ignore the building regs angle and say it was not suitable for the influences likely to be encountered under regulation 512.2. of BS7671.

If I fancied an argument that is.
 
I'd probably ignore the building regs angle and say it was not suitable for the influences likely to be encountered under regulation 512.2. of BS7671.

If I fancied an argument that is.

Good argument. But that's something you can argue about, like we do. The NHBC guidance, which the builder will use, is specific. That said think the OP said it was directly above the draining board?

Talking of OP...................................................................
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
gloucetser

Thread Information

Title
New build house, socket near sink
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
46

Advert

Thread statistics

Created
dave992,
Last reply from
Midwest,
Replies
46
Views
39,133

Advert

Back
Top