Hello people
Testing a new RFC yesterday. Property is a bungalow cable run in loft . All tests perfect apart from IR readings ok all between 400 & 600 meg but new cable would expect nearer >999 Checked cable run as mostly accessable and no damp or new plaster. Only thing is it was extremly hot in loft yesterday do you think think this could effect readings.
Cheers.
Neil
 
Cheers Tel. Not to worried just that it must have been near 90 degs in loft , well bleeding hot anyway just wonder if that would effect result in anyway. Ta
 
Have you considered that it might have been your test equipment affecting your readings?? lol!! All electronic equipment is affected by environmental conditions.

So Yes, temperature and/or humidity will also affect an installed cables IR readings, among others!!
 
In the old dark days we were taught test methods and reliability.

MTBF also got the nickname the “bathtub theorem” because if you draw a graph it is bathtub shaped. The newer something is, the more chance of it going wrong.

View attachment 12539
 

Reply to new circuit ir test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top