Hi guys

I Have been asked to install wiring for a new hob, with extractor hood, the hob instructions say it requires a 30A minimum supply, the hood is only about 200w

Would it be ok for me to install a dedicated ring circuit, in 2.5, for both items, or do i have to give the hob its own 6mm radial?

Any responses appreciated!
 
Ok thanks, I havent physically seen the hob yet to see the ratings plate but assuming for now the cable can carry the current, are there any other reasons you can think of I cannot use the method mentioned, regs wise?
 
and why a 1.5mm for the extractor.....1.0mm more that sufficient here.....
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

4MM would probably do for the cooker, but 6MM is better in case of changes down the line, bigger hob fitted etc. With such a short run the cost of cable is going to be minimal anyway.
 
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

4MM would probably do for the cooker, but 6MM is better in case of changes down the line, bigger hob fitted etc. With such a short run the cost of cable is going to be minimal anyway.
well that sounds fair.....its just that i keep seeing 6mm mentioned in this forum.....when it just aint necessary.....it also says to me that there are some coming in here asking away.....who cant get their head around diversity and/or cable calcs......
 
Last edited by a moderator:
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

Besides 1.5mm cable is the minimum csa allowed for S/O's or FCU's.

see App 15/15B (BGB) the Note at the bottom right of the page.

reg 524.1 and table 52.3 (BGB)
 
Last edited:

Reply to New Cooker circuit, is this ok? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
They need to put in a suitable test facility. This should have been part of the design putting in two separate circuits suggests they are not...
Replies
10
Views
3K
  • Question
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
  • Question
I appreciate the input on this. I decided it is not a good idea, and will spend the money and time to install a new dedicated circuit with...
Replies
5
Views
1K
  • Question
If multiple socket outlets are connected via one length of 2.5mmsq then it is not protected against overload by the 32A device in the CU. (You...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks