Hi guys

I Have been asked to install wiring for a new hob, with extractor hood, the hob instructions say it requires a 30A minimum supply, the hood is only about 200w

Would it be ok for me to install a dedicated ring circuit, in 2.5, for both items, or do i have to give the hob its own 6mm radial?

Any responses appreciated!
 
and why a 1.5mm for the extractor.....1.0mm more that sufficient here.....
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

4MM would probably do for the cooker, but 6MM is better in case of changes down the line, bigger hob fitted etc. With such a short run the cost of cable is going to be minimal anyway.
 
In a 4 metre run the savings aren't worth noting. And I generally would have 1.5mm to hand, not 1.0mm:goofy:

4MM would probably do for the cooker, but 6MM is better in case of changes down the line, bigger hob fitted etc. With such a short run the cost of cable is going to be minimal anyway.
well that sounds fair.....its just that i keep seeing 6mm mentioned in this forum.....when it just aint necessary.....it also says to me that there are some coming in here asking away.....who cant get their head around diversity and/or cable calcs......
 
Last edited by a moderator:

Reply to the thread, titled "New Cooker circuit, is this ok?" which is posted in UK Electrical Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top