Hi everyone. Im on a job thats really boggling me.
So old freestanding electric cooker was tripping when hot plates are on for about 15-20mins. I did the insulation tests on the cables when disconnected at board. 999+ reading. So I thought ok must be cooker. Estate agents orders new one. I install new one and same thing happens.
So I tested cables again. Wiring is 5years old. Perfect readings all the way from consumer unit to the cooker itself when hot plates are cold.
When I put the hot plates on for 5mins, I test again at the cooker. Resistance drops o about 400ohms. When I have plates on longer about 10mins. Resistance drops to 4-5 ohms.
I have on for longer and eventually rcd trips. I test the resistance at the cooker on each individual plate and it's showing 0.
Same readings I'm getting between the earth to neutral earth to live. Is this normal for hot plates?
I have tested the rcd trip times. I've moved the cooker over to the other rcd, still tripped.
Its a Toolstation axiom dual rcd board. Maybe these rcds can't handle cookers. But then it's been working fine for 5 years. I'm thinking the new cooker is also faulty.
If anyone has any thoughts and ideas please.
Just want to check, are these numbers are correct, or do you mean M ohms? And what have you measured the resistance between?
OK, so just to be sure I'm clear...
1. You've got end to end conductivity down each separate conductor in the supply cable
2. When cold there is acceptable resistance between the three combinations L-N, L-E & N-E
3. When hot, (2) changes.
When it's hot/faulting, where are you measuring the new IR readings from? The conductors with the oven removed or some place on the oven with it still in circuit?
Have you clamp tested the cpc at the board to see what leakage current is happening when it's running?
As per Rockingit above.
Not ignoring it could be the supply wiring, but it's vaguely possible that both the old cooker had a genuine fault, and the new cooker has earth leakage because it's been sitting in a damp warehouse for the last year, so has moisture in the elements. That should eventually bake out after several cycles, maybe after resorting to running one at a time.
When you checked if the rcd tripped with the new cooker, were all the hotplates on together, or were you testing with one or two? Does the oven do the same?
Edit: The topic of moisture in oven elements crops up here quite often. I seem to remember a post by Lucien ages ago explaining that when an element containing moisture is first turned on, the heat drives moisture towards the colder ends of the element, and this results in the insulation resistance falling to start with (ie the higher concentration of moisture at the live end leads to higher leakage current L to E). So far I've failed to find that post I'm afraid.
You really need a low amp clamp meter round the live and neutral,this will let you see where the leakage comes from,turn off all other Circuits on the shared (RCD).
Idealy run each element on its own for 10 or more minutes
So when it gets hot, I get 0 reading at L-E and N-E.
When it's hot. I'm testing resistance at the 45a wall switch. Making sure the neutral is disconnected at the c/u. The readings are good until I turn any of the plates on from the cooker knobs.
I haven't clamp tested yet. I will do that when I go back.
Wouldnt I need to clamp the cpc as leakage would be down the cpc conductor?
If you are measuring with an IR meter, that won't display below 20k ohms I believe, just says 0
Got a multimeter?
EDIT: to trip an RCD, the resistance of the fault needs to be below around 15k ohms. If it's a wet element, that's the sort of value you might expect to find using an ohmmeter, and it would probably be gradually changing.
Either. If you clamp round both L and N, the clamp meter should show the difference between L and N current, ie the leakage
You need to disconnect the cooker (or be testing separately each side of the DP isolator - that’s the only way you’ll know which side is failing when hot - supply cable or load.
I think I've done that already. At the double pole isolator I test the supply side and I get infinite readings. When I test the load side with the isolator off it shows 0 when plates are hot.
What instrument are you using that shows 0 Megohms?
And just for interest, are hotplates still tripping the RCD in the same time, or is it "getting better"!
I'm using megger 1711 multitester.
Tenants been using cooker for couple weeks now so I doubt theres moisture buildup left.
Yesterday I put the cooker on a plug top, plugged into the ring circuit and told tenant to use only max 2 plates. I had msg from them saying it tripped again. So now it comes down to the rcd or faulty cooker. I'm thinking of putting the cooker on its own rcbo too what happens.
If you have a reading of 0 ohms to earth when the plates are hot you have a faulty cooker , I take it that you have tried each plate individually. If you hadn't got a RCD in circuit I would have expected that it would have gone bang.
So the cooker tripped when plugged in the sockets ring circuit. I got a dedicated rcbo and that tripped as well. Definitely the new cooker is faulty. I've told agents to send it back and get new one.
Bijlee,
EddieB,