Firstly, I am not an electrician so please go easy on me and if I have omitted anything please ask.

We've had a new cooker and induction hob installed from Ikea. Here's some information on the setup :-
  • New consumer unit, 100A 30mA RCD feeds 8 MCB's
  • First MCB in line from the RCD is a 40A MCB for the cooker
  • New cable from the above MCB to cooker switch (10mm)
  • New cable from cooker isolator switch to cooker terminals behind cooker (10mm)
  • Induction hob wired in to cooker terminals (2.5mm)
  • 13A fused spur wired in to cooker terminals which feeds the cooker (hard wired cable from cooker)
The RCD is intermittently tripping and it "appears" to be the cooker/hob causing this. Here is some information about the various situations after some troubleshooting :-
  • Cooker and hob work fine, appear to have no issues
  • The RCD has never tripped whilst the cooker or hob have been in use, even at the same time
  • The RCD has never tripped whilst the cooker switch has been turned off
  • The RCD has tripped only once when turning on, but mostly when turning off
  • The RCD trips hours after the cooker/hob has stopped being used, but isolator switch remains turned on
  • On one occasion I couldn't get the isolator switch to turn on without the RCD tripping. After switching off the fused spur to the cooker (leaving only the hob) the power could be turned on. As soon as the fused spur to the cooker was turned on, the RCD tripped again
So after troubleshooting the above, I assumed it was the cooker causing the issue so phoned Ikea and they sent a replacement. However, this is physically damaged so also needs to be returned. In the meantime I have read up on earth leakage and got myself an earth leakage meter as there are a lot of recommendations that maybe the leakage is nearing 30mA throughout the house and it may be the hob/cooker are causing this to go over the threshold.

I've not had time to test everything throughout the house yet but I've measured the hob earth leakage and it's 5mA. Considering the whole house is limited to 30mA, this seems a bit high to me. What is the "normal" leakage for an appliance like this? I will test the cooker shortly too and I suspect that this could be "high" as since the cooker has not been connected at all, the RCD hasn't tripped with only the hob connected.

Any comments appreciated.
 
Thanks, that's what I was looking for - an actual suggestion :)

So, get rid of the 100A RCD for 100A main switch and replace the MCB's with RCBO's?
that's an ideal solution, albeit expensive. what make is the board?
 
Yes, I have paperwork. Again, what regulations does it not comply with?

If you believe the RCD tripping issue lies with the consumer unit installation quality then that's fine. Otherwise, I'm being led down the wrong path and still have a potentially faulty hob/cooker. When you guys have tested hobs/cookers/appliances etc. previously, what would expect the earth leakage to be? Is an item considered faulty if it's above a certain mA?

Best you review the results and let us know what the IR readings are

There is no way you can say its "fine"

No - impossible to state - unless of course its leaking over 22mA

and may I add with a MFT you can't test the RCD either
 
Is it possible/within regs to have 1x RCBO protecting just the cooker circuit and an RCD protecting the other circuits?

You've already stated that there is a space restriction.

Best you get the spark back who did the install to do some more tests and then advise you on how best to make the installation comply with the regs.

Personally I'm very doubtful a spark was involved ... but you could try and convince me
 
Last edited by a moderator:
Is it possible/within regs to have 1x RCBO protecting just the cooker circuit and an RCD protecting the other circuits?
Not really Maffoo. No electrician is going to fit it this way for a main consumer unit. Also, it would be pretty irresponsible of any electrician to give you step by step instructions on how to do it properly as (no offence intended) it sounds like you may try and do it yourself and even though you may be able to get it working there is lot more too it than that.
My advice is to get an electrician to change the current configuration of the board to all RCBO's. If you wanted an RCD protecting some circuits and some RCBO's protecting others then it is doubtful your current board has the capability to do that as it will probably only have one neutral bar in it.
 
Last edited:
So you've got a new fuseboard plus at least 1 circuit - so not only should you have an EIC (electrical installation certificate) plus a Building Control Part P compliance certificate.

Here's hoping

So @maffoo ............ a "dislike" - what for ......... pointing out the paperwork and compliance certificates you should have

Rather odd feedback IMHO
 

Reply to New cooker tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
453

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top