What you got to remember that Reg 544.1.2 states shall be made as near as practicable to the point of entry. That 600mm also where as practicable, it then goes on to say that the only certain thing is it must be made before any branchwork. So in theory 600mm is best, in the real world bond in the best position before a branch, so if that is 3 meters then 3 metres it is, just do it before any branch.

Now the bonding to that flat must be done in the flat, so forget the cellar. You will most likely find that it it may be 6mm where you can see it but it may have a joint and a length of 1mm inserted. I personally have seen this a 6mm cable from the gas pipe entry in the kitchen and when it went under the floorboards there was a connector block and a 7metre run of 1mm^ to another connector block and then 6mm again to the MET.

Now the bonding for a TN-S clearly states in reg 544.1.1 that it must be no less than half the CSA of the protective conductor. The protective condutor for the installation is either worked out by reg 543.1.3 or by table 54.7. If you have worked out that your protective conductor can be 10mm^ then you can use a 6mm^ as per reg 544.1.1, but you have to be able to prove this with your calcualtions if ever anything went wrong
 
Did you null meter before testing using a long lead from main earth to gas and water? sounds like readings obtained included the wander lead.
 

Reply to New CU, but bonding not 10mm2. What to do?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top