Have a job coming up to supply a new distribution board. I am planning on running a 25mm 4 core swa and 16mm earth of a distance of 30mtrs from incoming supply to new board. The supply is 3 phase 100a tncs. I was thinking of coming out of the Henley blocks into a 100A Glasgow switched fuse and then the swa out of the switched fuse to a 80A 30mA 4pole rccb supplying the new board. Thoughts?
 
Have a job coming up to supply a new distribution board. I am planning on running a 25mm 4 core swa and 16mm earth of a distance of 30mtrs from incoming supply to new board. The supply is 3 phase 100a tncs. I was thinking of coming out of the Henley blocks into a 100A Glasgow switched fuse and then the swa out of the switched fuse to a 80A 30mA 4pole rccb supplying the new board. Thoughts?

16mm separate earth is most likely oversized and a complete waste of time and money to boot, if main bonding is required at the sub-board then a 10mm bond will be required, but not if no main bonding is to be connected there.
Glasgows are fused switches not switched fuses, there is a difference.
An 80A RCD is no good on a 100A supply.
A 30mA RCD covering a whole board is just plain ridiculous.
 
I think the best option is use individual rcds if required. So instead of the 16mm earth would you just use the swa?

Using a seperate earth for the size you suggested wouldn't normally be required although it may be necessary in certain circumstances like reducing Zs due to high upstream initial values or bonding requirements may warrant running a seperate earth.
 
Had a look at the current set up. There is a main DB and 2 sub DB's. 1 of the sub boards is supplied from a fused switch and the other one is supplied from a 63A TP MCB. I would have thought both sub boards would have been supplied by fused switches.
 

Reply to New dist. board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
922
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
710
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top