[h=2]new eco tec plus combi boiler wiring[/h]
evening all.


ive been asked to connect the mains supply and room stat to the new valliant combi boiler. Connections are different to what im used to.

Am I correct that the room stat connects to the RT terminal next to the 230v terminals?


Ive copied and pasted the manual. The diagram is on page 32.

Electricians Resources - downloads that electricians find useful - http://www.electriciansforums.net/resources/
thanks​



Read more: http://www.electriciansforums.net/e...c-plus-combi-boiler-wiring.html#ixzz1yquZlNgI
 
Last edited by a moderator:
Assuming you have a stat that will operate at 24V yes (most will do 24-230V, check stat instructions).

You don't say what the room stat is and whether you're incorporating a separate programmer (or just using a combi stat). How is it being wired?
 
Thanks for reply topquark.

I spoke to technical support and they talked me through how to connect. I fitted a honeywell stat 230v. I removed the RT link on the 24v side and looped live terminal to my room stat and back to the 230v RT terminal.

Boiler fired up.
 
Yes it got me this one, you get no voltage reading on the meter on the 230 stat side and the book doesn’t tell you to link it out
 

Reply to new eco tec plus combi boiler wiring in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

S
  • Article
Electrician Boiler Fault Boiler Fault I’m hoping someone can help with this boiler problem. Couple have just moved into a house that has a Grant...
Replies
0
Views
238
S
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top