srl-8

Hello Guys,

I will be installing an electrical supply to a new garden office and I want to run my thoughts about my installation past you all, to see if I have got this right in term of cable selection and load, or if anyone can suggest another way of doing this…

The Office will use the following load, I have rounded all amounts up to be safe.

3 x 1.5 kw heaters = 4500w = 20Amps

8 x 50w down lights = 400w = 2 Amps

4 x computers = (allow 250w per machine) =1000w = 5 Amps

Possible additional usage (microwave/printer/phone charge/fan etc) allow approx 1000w = 5amps

TOTAL AMPS = 32



I plan to install a 10mm PVC multi-core cable from Fuse board, (Protected by a 40 or 45 amp MCB or RCBO) through the house, until outside, then change to 10mm SWA up to the new installation. (Approx 15 meters away)

A new garage board will be installed with rcd in the new office, protecting the relevant new circuits.

(It is yet to be decided if client wants to have a new main fuse board in the house or install a separate unit fed from the Henley block.. The old fuse board is re-wireable fuses and non-rcd. I believe the earth arrangement is PME at this stage.



I would like your opinions and suggestion please

Thanks!



 
Hello Guys,

I will be installing an electrical supply to a new garden office and I want to run my thoughts about my installation past you all, to see if I have got this right in term of cable selection and load, or if anyone can suggest another way of doing this…

The Office will use the following load, I have rounded all amounts up to be safe.

3 x 1.5 kw heaters = 4500w = 20Amps

8 x 50w down lights = 400w = 2 Amps

4 x computers = (allow 250w per machine) =1000w = 5 Amps

Possible additional usage (microwave/printer/phone charge/fan etc) allow approx 1000w = 5amps

TOTAL AMPS = 32



I plan to install a 10mm PVC multi-core cable from Fuse board, (Protected by a 40 or 45 amp MCB or RCBO) through the house, until outside, then change to 10mm SWA up to the new installation. (Approx 15 meters away) What type of cable would this be? would depending on the cable and erection method, need RCD additional protection. Is the CPC the same size as the LIVE conductors?

A new garage board will be installed with rcd in the new office, protecting the relevant new circuits. If the multi core cable in the house needs additional 30mA protection will you have an issue with RCDs in series

(It is yet to be decided if client wants to have a new main fuse board in the house or install a separate unit fed from the Henley block.. The old fuse board is re-wireable fuses and non-rcd. I believe the earth arrangement is PME at this stage.



I would like your opinions and suggestion please

Thanks!

Will this office have services, such as a bathroom and therefore a water supply, is the construction of the building metallic at all, What type of earthing system do you have?
 
Can someone please confirm or correct me, that my cable sizing is correct, based on my info in my first post. I dont have my books to hand, so cannot confirm 10mm cable rating....
 
10mm cable is fine, it's the cpc of the 10mm that will be the problem as in twin and earth the cpc will not be 10mm. Hence why you were advised to run a separate 10mm cpc with the T+E or use 3 core swa for the whole cable run.
 
Out of interest, is that a reg requirement, the upgrading of the T+E earth?
I would imagine the 10mm T&E would prolly not be chased in a wall so wouldn't need RCD right?

I take it the office is a wooden shed type building?
I've done few of these and usually have the sockets fed from external black PVC conduit at the back of the shed and the lighting surface clipped T+E with conduit/trunking for the switch drops. Gives a nice balance of cheap/neat/protected.
 
Out of interest, is that a reg requirement, the upgrading of the T+E earth?
I would imagine the 10mm T&E would prolly not be chased in a wall so wouldn't need RCD right?

I take it the office is a wooden shed type building?
I've done few of these and usually have the sockets fed from external black PVC conduit at the back of the shed and the lighting surface clipped T+E with conduit/trunking for the switch drops. Gives a nice balance of cheap/neat/protected.

Upgrading of the T+E CPC would be required under regulation 543.1.1, if the CPC size was too small for the fault current.

To be honest you may find the 4mm CPC large enough, the only problem is that because it seems to be a TNC-S system, you may just want to do the adiabatic to make sure
 
The 10mm will be run under floorboards in the house and the swa will be burried.
I think i will run 10mm 3 core swa, and this will give me the 10mm earth to be sure.

good advice
 

Reply to New garden office, Cable selection and method...? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
642
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
635
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks