Hi,

just moved in, and I find this, and haven’t seen anything like it before.
Is this 3 phase?
any concerns at all?
There is a heated pool outside. Could be needed for the pool heater.

1st post, and I thought I’d seek some guidance on here. Many thanks for replies.
 

Attachments

  • 1A3EDB6A-8BF3-46C6-A1E6-7CAC45B27FAF.jpeg
    1A3EDB6A-8BF3-46C6-A1E6-7CAC45B27FAF.jpeg
    354.1 KB · Views: 146
Yes large switch with the red yellow and blue circles is a 3phase switched fuse . the unit marked up pool is single phase 1 way consumer unit. Do you have a picture of your main electric meter ? As SJD says I would want to check where those disconnect cables go to or come from.
 
Yes large switch with the red yellow and blue circles is a 3phase switched fuse . the unit marked up pool is single phase 1 way consumer unit. Do you have a picture of your main electric meter ? As SJD says I would want to check where those disconnect cables go to or come from.
Thanks, I’ll have another look when I’m at the property tomorrow.
Looks like I should get those cables checked out and removed by someone qualified.
On the plus side I’m now thinking 3 phase could come in useful when I go electric car. Not yet however.
 
Certainly looks like a 3 phase supply , but intrigued to know what looks like only Red and Yellow phase stickers on the enclosure to the right of the RCD so taped cables 2phases + N + g/y earth?
 
That's a 3 phase residual device, top right, one phase to Wylex single phase RCD unit for the pool.
It looks like the unused switch/breaker was for 2 phases (red, yellow) and N tails seem to be disconnected and taped. The CU is labelled 'blue', with another RCD....It may be that blue phase only is in use.
Interesting to see the metering system. It needs some investigation and a bit of sorting out, for sure, but looks pretty sound in general.
 
That's a 3 phase residual device, top right
Surely you mean 2nd from top right, the Wylex unit?
If you are right about the unit top right being another RCD unit there doesn't appear to be a lot of discrimination going on as doubt the 3ph RCD is S type but job to tell from the photo!
Perhaps disconnected tails were something to do with the E7 supply ?
 
That's a 3 phase residual device, top right, one phase to Wylex single phase RCD unit for the pool.
It looks like the unused switch/breaker was for 2 phases (red, yellow) and N tails seem to be disconnected and taped. The CU is labelled 'blue', with another RCD....It may be that blue phase only is in use.
Interesting to see the metering system. It needs some investigation and a bit of sorting out, for sure, but looks pretty sound in general.
Here’s a pic of the meter.
What’s a radio teleswitch anyone?
 

Attachments

  • D184B76B-23B9-4167-AE4E-8C356A599E20.jpeg
    D184B76B-23B9-4167-AE4E-8C356A599E20.jpeg
    783.2 KB · Views: 91
Presumably the meter cabinet is within a few metres distance of the consumer unit? At first I had visualised the 3-phase switchfuse and its 4-pole RCD as the incomer but evidently it's an outgoing submain therefore there are no cascaded RCDs. It looks like the teleswitch output is Henley-blocked to two pairs of tails, one of which probably goes to the Wylex SF far left. Therefore the disconnected circuits top right appear to have red phase on E7 and yellow on 24h, so perhaps a complete storage heating system has been decommissioned.
 
Presumably the meter cabinet is within a few metres distance of the consumer unit? At first I had visualised the 3-phase switchfuse and its 4-pole RCD as the incomer but evidently it's an outgoing submain therefore there are no cascaded RCDs. It looks like the teleswitch output is Henley-blocked to two pairs of tails, one of which probably goes to the Wylex SF far left. Therefore the disconnected circuits top right appear to have red phase on E7 and yellow on 24h, so perhaps a complete storage heating system has been decommissioned.
Good chance, looking at the second photo. They may be back to back, even. Blue phase on the right (meter box) going in to the CU on the left. If so, what's the Exel feeding?
May be an upgraded plant room for the 'heated' swimming pool, looking at the 45A SP Wylex....
 
Presumably the meter cabinet is within a few metres distance of the consumer unit? At first I had visualised the 3-phase switchfuse and its 4-pole RCD as the incomer but evidently it's an outgoing submain therefore there are no cascaded RCDs. It looks like the teleswitch output is Henley-blocked to two pairs of tails, one of which probably goes to the Wylex SF far left. Therefore the disconnected circuits top right appear to have red phase on E7 and yellow on 24h, so perhaps a complete storage heating system has been decommissioned.
Yes, the meter cabinet is on an outside wall of the utility room near the consumer unit inside.
Thanks for all the commentary here, obviously the right forum.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kings Lynn
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
New home. Is it 3 phase?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Jimjam928,
Last reply from
Jimjam928,
Replies
15
Views
2,006

Advert

Back
Top