G

glasgospark

new house guys with a new heating system through mcs real scheme

3 phase supply run into house the pump is the only piece of equipment requiring 3phase ,

question is looking for best way to do this was thinking give the house itself the normal dual rcd db then from 3phase mains to lucy blocks fuse down for pump.

pump is situated in the same location as main cable head ,

4kw 32a 3phase supply required via rotary isolator


any views ?
 
Yes, but your only providing over current protection for the supply to the heat pump. As such, from the Henley block you take a 6mm2 for example to the switchfuse. The 32A fuses protect that cable from overload, the 100A fuses provide short circuit protection.

If you consider a busbar chamber, you wouldn't size everything fed from it to the size of the incomer.
 
You only require one point of isolation. This is primarily the cutout. I agree that one switch in front of everything is best, but only if the customer will pay!

Why would it be a 100A switch? You can get 32A switchfuses. Socomec make them among others.

[ElectriciansForums.net] new house 3phase heat pump
 

Reply to new house 3phase heat pump in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top