A

ash_s3

Just been to a new house (5 years old) which had no main equipotential bonding to the incoming water. Gas was bonded with 10.0mm
Checked on original EIC and water service box was marked N/A
All pipe work inside the house is copper but the supply pipe is plastic up to main stop tap

Surely this isn't right?
 
Correct, it is not right, the internal metal pipework should be bonded.
There's an unless figure but I can't remember what it is
 
I though it needs bonding unless ALL internal pipe work is plastic.
Might see if neighbors houses are the same.
I assumed there would be no issues with this property with it being so new.
Dual rcd board - check
gas bond - check
water bond - err... It must be here somewhere!
 
From OSG "There is no requirement to main bond and incoming service where the incoming service pipe and the pipework in the installation are both of plastic. where there is a plastic incoming service and a metal installation within a premises main bonding is recommended unless it is confirmed that any metal pipework within the building is not introducing an earth potential."

IF an IR test between MEt and the metal pipework give a value <22Kohm then the metal internal pipework should be bonded, if it is greater than that then there is no need to bond as it is not introducing an earth potential.

There is some variation in the IR figure depending on who you listen to but generally if it is not connected to earth then there is not need to bond plastic incomers.
 
So am i right in thinking that if the main feed, stop tap and (for arguments sake) 1st 6m of consumers pipe is plastic, but the rest is copper you bond your main bonding as soon as it changes to copper?

I have never actually worked on a property like that before so its new to me.
 
I would carry out a continuity test. And if over 23k ohms then it does not need bonding. Taking this from a 'safe' touch current of 10mA.
230\0.01= 23,000 ohms

My opinion of the OSG is proving to be more true each time I hear stuff from it. I don't like it to say the least.

Yes if it's all plastic and you can see it is. Then it's pointless testing.
But if there's any copper id check as its your --- on the line if it ain't right.
 

Reply to New house, no main water bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
166
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I like your way of thinking.
Replies
6
Views
725
loz2754
L
If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
451

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top