Jimmyb

hello all, can someone please advice me the best way of filling out EIC form when doing sub-main supplies.

I doing a log cabin installation and i have made the cabin a tt due to the supply being 30 meters away and being TN-CS.

The bit I'm not sure on is where, if at all, do i put the earth rod resistance of the cabin as I'm only recording the supply characteristics and i thought this maybe should noted some where.
I did a house rewire and new garage installation last month and noted on the certificate garage supply on it own line and wrote on under Zs colum the earth rod resistance and then started a new line with the garage circuits and after talking to a few others I'm now think i may of done it wrong and maybe should i have done 2 certificates but i dont really know so was hoping you guys could help me out with this one as i dont want to get it wrong especially twice.

thanks for any advice's
jim:)
 
You mention sub-main, I take you have a second board for the cabin then? If so then you would have a second schedule of test results, as each board must have its own schedule. So...

1 x page for client details etc.
1 x sheet for supply characteristics and earthing arrangements
1 x inspection schedule certificate
2 x shedule of test results

so on the second schedule of test results you would state it's a TT system and make a note of its earth electrode resistance.

Hope this helps!:D
 
Thanks for the quick reply, i think ive got it but just check i use elseca sheets which has on :-

sheet (1) - cilent details, supply characteristics and particulars of installation

sheet (2) - Shedule of items inspected and installed circuit details for 9 circuits

sheet (3) - Continuation sheet

so as i as understand i would want 1 x sheet (1) , 1 x sheet (2) with details of submain and a seperate continuation sheet ( sheet (3) ) for log cabin just showing circuit test results to which i make a note of earth rod resistance some where or do i use 1 x sheet (2) again

sorry to be a pain and thanks for replying brightspark
 

Reply to New Installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
689
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top