New kitchen, live earth fault!! | Page 2 | on ElectriciansForums

Discuss New kitchen, live earth fault!! in the UK Electrical Forum area at ElectriciansForums.net

J

Jeff.wd

Hi.. We have just had a new kitchen fitted, a few sockets moved, led lights, new supply for the electric oven and a rcd board fitted.
They told us they had checked the supply before they started and everything was fine, we knew to meet regs the board needed replacing, during installation the kitchen fitter drilled through a cable, getting a large flash but no fuses had blown (still the old board at this point) he told us straightaway and said he would get the electrician to check it, when the electricians returned to finish the kitchen and fit the board they told us the cable was fine and they had crimped it, ( would that mean removing some of the plaster and conduit to access the cable, in order to crimp it.)
The next day when the gas/plumber was fitting the new gas hob, he was getting tingling shocks from the gas pipe, when we plugged the hob into the socket for the ignition, (with the socket switched off), it tripped a rcd on the new board, we spoke to the electrician and he was convinced we had a faulty hob, he told us to try another appliance in that socket, we tried a hairdryer and it worked fine with nothing tripping. We then plugged the hob in and all appeared okay, over the weekend my partner received several shocks from the metal sockets above the worktops, we informed the electrician and he said he would come after the weekend.
On arrival he thought it would be a short visit and easily sorted, after 4 hours of trying to diagnose the fault, we now have been told that there is 80 volts leaking via earth to the bonding, they said the kitchen is testing and okay and the downstairs/kitchen ring is okay through the hallway, once they test in the lounge they pick the fault up there? They left saying they would phone colleagues and technical teams for ideas.
They are coming back next week to try and solve the problem, they said the conclusion is either a pressure fault or possibly a badly wired plug on a appliance?
Now my thoughts, all cables from the main board in the garage run up to the ceiling cavity, I presume the feed and return for the downstairs/kitchen ring, will come down from the ceiling go under the floorboards and return else where, the cable that was drilled through, comes from the ceiling going directly down the wall (no sockets etc) then under the floorboards,I asked them what the cable that was, they said it is not part of the kitchen ring, I can't think that it can be anything else other than part of the downstairs ring? Would drilling into that cable possibly cause a surge, resulting in a fault some where on the downstairs ring?
They want to charge us for diagnosing and repairing,unless it was caused by the work in the kitchen!!
Many thanks for any help/advice or guidance.

Cheers Jeff.
 
So the upstairs sockets aren't protected by a RCD - why not? The installation doesn't comply with the regs....

Can you post a picture of the fuseboard?
From rcd readings looks like a high integrity board. Upstairs sockets won't be used out of doors, maybe he is on an old set of Regs:)
 
So the upstairs sockets aren't protected by a RCD - why not? The installation doesn't comply with the regs....

Can you post a picture of the fuseboard?
He was a kitchen fitter, you can't expect it to be right when you employ those cowboys to do electrical work.
 
So the upstairs sockets aren't protected by a RCD - why not? The installation doesn't comply with the regs....

Can you post a picture of the fuseboard?
Hi again, kitchen sockets should read kitchen and downstairs sockets, house sockets should read upstairs sockets!!

[ElectriciansForums.net] New kitchen, live earth fault!!
 
H
Im betting there was a earth leakage fault with the upstairs sockets existing, there is absolutely no reason to segregate them away from any rcd protection otherwise... no self respecting qualified competent electrician would do what this 'electrician' has done.
They did say there was a neutral fault on the upstairs sockets, could this be the reason. Could that simply be a badly wired plug?
 
My brother had a similar thing on his kitchen a few years ago, earthing conductor was loose at pme terminal, must have been like it years and someone must have inadvertently moved it.
 
That image hardly inspires confidence, apart from the fact that the "house" sockets do not have RCD protection as previoulsy mentioned. Ii doesn't help us with your original question, but it gives us an idea of how your 'electician' spells quality!
 

Reply to New kitchen, live earth fault!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
738
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top