Prestatyn
Hi, installed a new lamona cooker hood as part of a kitchen refit. Connected to 6a lighting circuit on switched 3a fuse supply. All tested fine, but use any function on hood, and dual rcds trip. Checked wiring, all ok, fused switch is new click, but since not tripping when this is switched on, sure it’s not that. Fused switch as it’s own independent cabling. Before I remove extractor And frog march back to howdens, any one any constructive ideas?
 
Hi, installed a new lamona cooker hood as part of a kitchen refit. Connected to 6a lighting circuit on switched 3a fuse supply. All tested fine, but use any function on hood, and dual rcds trip. Checked wiring, all ok, fused switch is new click, but since not tripping when this is switched on, sure it’s not that. Fused switch as it’s own independent cabling. Before I remove extractor And frog march back to howdens, any one any constructive ideas?
Where exactly have you connected the cooker hood to the lighting circuit?
 
Out of interest why did you feed it from the lighting circuit if you have taken it direct from the consumer unit? I assumed you had taken a feed from the lighting circuit because you could pick it up near to the location of the hood.
 
QUOTE="Pete999, post: 1379502, member: 72029"]Where exactly have you connected the cooker hood to the lighting circuit?[/QUOTE]
Have you connected the N to the corresponding N busbar? you may have created a "borrowed N condition"
 
QUOTE="Pete999, post: 1379502, member: 72029"]Where exactly have you connected the cooker hood to the lighting circuit?
Have you connected the N to the corresponding N busbar? you may have created a "borrowed N condition"[/QUOTE]
Wisps gold to that man, I had indeed borrowed neutral, problem resolved, thank you sir
 
Of course, you do know that connecting directly to the consumer constitutes a new circuit??

This work therefore needs to be notified to the local authority, and of course you'll be providing an installation certificate that confirms that all of the tests you have done meets the requirements of BS7671?

Of course you will:rolleyes:
 

Reply to New lamona cooker hood tripping both rcds in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top