just a quick one, I’m doing 18th edition next week but have been asked to quote for changing pendant lights for new stainless steel lights. Assuming all bonding, wiring and tests check out etc, does this now require an rcd?
 
Has anyone had a job under the 18th where they have had to alter or extend a lighting circuit that does not have RCD/RCBO protection (taking the reg regarding buried in walls out of the equation) how have you got over complying eg an RCD spur?
 
just a quick one, I’m doing 18th edition next week but have been asked to quote for changing pendant lights for new stainless steel lights. Assuming all bonding, wiring and tests check out etc, does this now require an rcd?
Has anyone had a job under the 18th where they have had to alter or extend a lighting circuit that does not have RCD/RCBO protection (taking the reg regarding buried in walls out of the equation) how have you got over complying eg an RCD spur?
Yes,had to wire new outside light so I fitted an rcd spur inside the house.There is talk on the iet forum that rcd spurs have a different BS number to normal rcbo,s and rcds,so there is some question about their use.
Regards,SW
 
Yes,had to wire new outside light so I fitted an rcd spur inside the house.There is talk on the iet forum that rcd spurs have a different BS number to normal rcbo,s and rcds,so there is some question about their use.
Regards,SW
It's a good point SW, but I thought it didn't state a BS number?
 

Reply to New light fittings, no rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
350
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
695
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top