To the op, have you quoted the dno's maximum typical value of 0.8Ω for tn-s or is that a measured value?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss New Member with an EICR question on max Ze reading in the The Welcome Forum area at ElectriciansForums.net
Might start calling you Lofty.
Hi - the 2 Ohms may be ok if the installation is designed for that, as you would for a TT. But in summary - ask owner to call DNO and request a safety inspection (free) as they've been told by an Electrician that it may be unsafe. My concern is it may indicate a deteriorating condition and Client could end up with no earth. Apologies to all who've already said this on the thread, or if you've already established it's 0.2 Ohms . Must have coffee ...Strange to not comment on it, but if all circuits have rcd protection, is that reading even a problem? Although if I measured that value then I'd still get the dno out for an unreliable earth, in case it gets worse.
Hi - the 2 Ohms may be ok if the installation is designed for that, as you would for a TT. But in summary - ask owner to call DNO and request a safety inspection (free) as they've been told by an Electrician that it may be unsafe. My concern is it may indicate a deteriorating condition and Client could end up with no earth. Apologies to all who've already said this on the thread, or if you've already established it's 0.2 Ohms . Must have coffee ...