Search the forum,
Discuss New meter tails running in 2 core 25mm swa and 16mm single earth in the UK Electrical Forum area at ElectriciansForums.net
tomodo
Hi everyone, i might be having to run new meter tails from meter box to consumer unit which is just under 3m run, i have used 25mm 3 core before and its hard to work with especially through joists. I was thinking about 2 core 25mm swa and a seperate 16mm earth to make life easier but then came to the problem of having to run all 3 cores through the same hole due to eddy currents when terminating, does anyone have any ideas on this or is it not possible? Thanks for reading
What is the run? I often just use some trunking and run the tails and earth in the trunking..
Since around the 17th Edition (or one of the amendments to it) it has been allowable for the protective conductor to be run alongside the SWA and through a separate entry in the ferromagnetic enclosure (a derogation from the general Regulation).
My greater concern would be how you intend to gland the SWA in a Permali Box however.
I might be missing something here, if you gland an SWA into a metal enclosure how would run the protective conductor through the SWA gland so it was through the same hole
Two immediate thoughts here: 1) What's your rationale for needing to use SWA on such a short run and 2) Does it actually need to be 25mm when 16mm will probably more than suffice? I.E...... are you making life hard for yourself here by not just using standard singles?
You can't, but a separate cpc was often run despite not being permitted. So JPEL/64 decided to expressly allow this for SWA - but it remains disallowable in all other circumstances.
Reply to New meter tails running in 2 core 25mm swa and 16mm single earth in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
I’ve got a job to quote for turning 1 big flat into 2 smaller flats. The DNO are looking at installing new meters in the communal area. I need to...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...