cambridge
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final.
1) In part 2 of the AMD2 small works cert, its wants Zdb supplying the final circuit. Does this mean the Zs for the ring final that I measure or the MaxZs 32A MCB which is 1.1?
2) for part 3 of the cert, is the new FCU 13A then in effect the new DB and therefore I would put in FCU, BS 1362, 13A?
3) Then for part 4 test results do I complete the R1+R2 just for the cable from the new socket to the FCU? will my max Zs be the rating for the 1362 fuse at 1.83?
Thanks for your help,
gordon daly
I’ll try to be more succinct. The 1362 fuse can be changed easily. If a lower fuse is used to achieve disconnection times, and is subsequently changed to a higher fuse, then its a poor design.
As said, I think we should agree to disagree.
Long time resurfaced thread!
expanding on your idea,
every device powered by a U.K. plugtop could be considered a design failure (other than 13A appliances) as the fuse protecting it could be changed.
But a plug ‘top’ BS1362 fuse is not protecting fixed wiring is it, so perhaps not a good analogy.
Reply to new minor works certificate for a fused spur in the UK Electrical Forum area at ElectriciansForums.net
For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
It applies to commercial if it shares the same supply as a dwelling.