taslaw

I have just bought a neff 2.9kw single oven; it replaces an oven that was hard wired on to a dedicated oven circuit on a 32a mcb with 6mm cable. My electrician says that he will just wire the new oven onto the same system. I am no expert, but thought that the mcb is too big for this oven , would it not be prudent to reduce the size of the mcb? thanks.
 
that 32A MCB is sized to protect the 6mm cable. nothing to do with the rating of the oven. nothing to stop you downrating it though. if you are concerned, then you could put it on a 13A FCU.

- - - Updated - - -

beaten by the monkey.
 
that 32A MCB is sized to protect the 6mm cable. nothing to do with the rating of the oven. nothing to stop you downrating it though. if you are concerned, then you could put it on a 13A FCU.

- - - Updated - - -

beaten by the monkey.
Thats the trouble with these monkeys, they can use their hands and feet to type :D
 
I would be reluctant to use a switch fuse on a 3 Kw load (you can but often see them burnt out ) its a dedicated circuit feeding a fixed load, use a 16 A mcb type b job done.
 
I have just bought a neff 2.9kw single oven; it replaces an oven that was hard wired on to a dedicated oven circuit on a 32a mcb with 6mm cable. My electrician says that he will just wire the new oven onto the same system. I am no expert, but thought that the mcb is too big for this oven , would it not be prudent to reduce the size of the mcb? thanks.

What do manufacturers instructions say regarding OCPD? These will have to be followed.
 
What do manufacturers instructions say regarding OCPD? These will have to be followed.

Not some of the manufactures instructions i've read you wouldn't!! lol!! Many of these instructions are based on European standards and wiring methods, rather than on your BS7671. Some, like the recently posted ''humidistat'' are just an outright joke!! lol!!
 
why go to the cost of replacing the OPD for a 16B?...
just use the existing MCB thats in there....the cable is protected and you dont need to go to the added costs of replacing the existing OPD...
 
Monkey,
just spoke to my sparky and he confirms what you have intimated, i.e. the 32a mcb with the 6mm cable is fine, despite less load with the new oven. Many thanks to all that have helped with their knowledge. Joanne.
 
Monkey,
just spoke to my sparky and he confirms what you have intimated, i.e. the 32a mcb with the 6mm cable is fine, despite less load with the new oven. Many thanks to all that have helped with their knowledge. Joanne.
Well i'm not just a pretty face you know :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
new oven
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24
Unsolved
--

Advert

Thread statistics

Created
taslaw,
Last reply from
GLENNSPARK,
Replies
24
Views
2,844

Advert

Back
Top